Hautec works fine here, although I don't exactly know, which TEM-board is installed. |
|
I tried to document my CSV file (15.csv) for further use here: Everything I do, is changing Raumtemp_soll and try to get rid of one error: "Niederdruck durch Sensor". |
|
@gruaGit thanks a lot for the answer, that is very helpful. Yes, I would be very interested in your Node-RED JSON, especially the decoding for the compressor contactor (K1), the heating mode (Heating/Summer) and the hot water setpoint. I have the same controller family (older revision, SW 0106) and see the same broadcast pages on the bus ( One thing that might help you as well: on my controller the hot water temperature can be read with the regular
In a CSV this is a plain read message (ID Thanks again for sharing! |
|
Update from my side (controller Working read messages (all
No answer on this firmware (the controller replies with parameter CSV (generated from
|
|
Correction to my earlier comment (I wrote that in
On our older firmware the heating value is The byte after the mode byte ( Still open: a reliable compressor (K1) status bit. The |
|
@mfore1 thanks, that's a really useful pointer - makes sense that it's the Status enum (02-053) rather than a flow setpoint. On my controller So far I've only seen I'll keep logging the byte alongside our Shelly power measurement and EVU terminal voltage and report back if I see values other than 0x00/0x25. |
|
Another data point on Second field = 10 is the controller's EVU-lock state. Our utility lock schedule (three windows per day) matches the field exactly: 55 → 10 at the start of each window, back to 55 shortly after the end. We confirmed it with a relay input in parallel to the EVU terminal as an independent reference. It reflects the controller's internal state, not the terminal voltage. On 17 Nov the controller stayed at 10 for over six hours although the release signal (230 V) was present on the EVU terminal and the relay confirmed it from 13:32. Re-seating the terminal block brought it back to 55. So 10 can also stay stuck after the window has ended, which is useful as a diagnosis: a stuck 10 outside the lock windows means the input does not reach the controller, in our case a bad plug contact. First field: 0 without demand, ~33–36 with demand. After the EVU case on 17 Nov the first field went to 34 at 20:00, but the compressor (measured via the power meter) only started about 15 minutes later. So for us the first field looks more like the demand than the compressor state. This may differ after an EVU lock versus a normal restart. I have not yet compared normal starts. No write access, read-only via ebusd 26.1. |


Uh oh!
There was an error while loading. Please reload this page.
Has anyone ever gotten a TEM SE6000 WPC with ebusd to work?
The TEM is installed in a Hautec heat pump. When using a Raspberry Pi 5 and the Elecrow eBUS Adapter Shield C6, I only get the message: “signal: no signal”:
ebusctl info
version: ebusd 26.1.26.1-7-g38db2d28
device: /dev/ttyAMA10, serial high speed, enhanced
signal: no signal
reconnects: 0
masters: 1
messages: 11
conditional: 0
poll: 0
update: 4
address 31: master #8, ebusd
address 36: slave #8, ebusd