I have the same unit ID and got it working. Sharing what I found in case it helps you and helps getting this into ebusd-configuration. Setup: recoVAIR VAR 350/4, scanned as Key finding: the WTW04 only answers to
|
| reg | value seen | meaning | type |
|---|---|---|---|
0000 |
19.4 | room temperature (written by the VAI every few seconds) | D2C + sensor UCH |
0100 |
9.56 | outdoor air into unit (SAI on display: 9.5) | D2C + sensor UCH |
0200 |
15.9 | supply air to rooms (SAO: 15.5) | D2C + sensor UCH |
0300 |
19.5 | extract air from rooms (EAI: 19.5) | D2C + sensor UCH |
0400 |
12.25 | exhaust air out of unit (EAO: 12.0) | D2C + sensor UCH |
0700 / 0800 |
~2060 / ~1460 | fan speeds in rpm (~3200 / ~3050 at 400 m³/h). Not yet confirmed which is supply and which is extract | UIN |
1500 |
312 | flow setpoint, written by the VAI. Steps of 0.4 m³/h on the 350: 312 = 125, 412 = 165, 1000 = 400 m³/h. Probably model-specific | UIN |
0900 |
0 | bypass position in % | UCH |
0a00 |
1 | heat recovery 1=on, 2=off (the VAI writes 1 regularly) | UCH |
4700 |
0 | negative-pressure (stove) protection, matches STOV: OFF |
UCH |
4500 |
90 | filter change interval in days (FILT 90) |
UIN |
4600 |
2 | days since filter change (FILT 2) |
UIN |
4d00 |
21962 | total yield (same value as the VAI's Yield) |
UIN |
2c00 / 2d00 |
time / date |
Note: writing the flow directly to c0 register 15 is pointless with a VAI attached, because it overwrites the value within seconds. Control has to go through the VAI.
VAI00: 15.vai.tsp works but is not published
src/vaillant/15.vai.tsp exists upstream (its header even mentions VAI00), but the @zz(0x15) is commented out, so there is no 15.vai*.csv on ebus.github.io. With SW0125 I verified:
- reads: NormalFlow 125, ReducedFlow 100, IntenseFlow 165, BypassFlow 115, HolidayFlow 90, FilterDays 2, FilterDaysAlarm 90, RoomTemp, Time and Date all match the display
- write:
HighDuration= 15 switches the unit to the intense level (setpoint 312 → 412) and counts down in minutes
@john30, would it be possible to publish 15.vai for VAI00? I'm happy to turn the WTW04 findings into a c0.wtw04.tsp PR if that's the preferred way.
Local CSV I'm using for the WTW04 (/etc/ebusd/vaillant/c0.wtw04.csv)
Used with a local --configpath /etc/ebusd --scanconfig:
type,circuit,level,name,comment,qq,zz,pbsb,id,*name,part,type,divisor/values,unit,comment
*r,
*w,
*u,
r1,recovair,,OutsideAirTemp,outdoor air into unit (SAI),,,b509,290100,ign,,IGN:2,,,,temp,,D2C,,°C,temperature,sensor,,UCH,0=ok;85=circuit;170=cutoff,,sensor status
r1,recovair,,SupplyAirTemp,supply air to rooms (SAO),,,b509,290200,ign,,IGN:2,,,,temp,,D2C,,°C,temperature,sensor,,UCH,0=ok;85=circuit;170=cutoff,,sensor status
r1,recovair,,ExtractAirTemp,extract air from rooms (EAI),,,b509,290300,ign,,IGN:2,,,,temp,,D2C,,°C,temperature,sensor,,UCH,0=ok;85=circuit;170=cutoff,,sensor status
r1,recovair,,ExhaustAirTemp,exhaust air out of unit (EAO),,,b509,290400,ign,,IGN:2,,,,temp,,D2C,,°C,temperature,sensor,,UCH,0=ok;85=circuit;170=cutoff,,sensor status
r1,recovair,,Fan1Speed,fan 1 speed,,,b509,290700,ign,,IGN:2,,,,value,,UIN,,rpm,
r1,recovair,,Fan2Speed,fan 2 speed,,,b509,290800,ign,,IGN:2,,,,value,,UIN,,rpm,
r1,recovair,,FlowSetpointRaw,flow setpoint in 0.4 m³/h steps,,,b509,291500,ign,,IGN:2,,,,value,,UIN,,0.4m³/h,
r5,recovair,,FilterDays,days since filter change,,,b509,294600,ign,,IGN:2,,,,value,,UIN,,days,
r5,recovair,,FilterDaysAlarm,filter change interval,,,b509,294500,ign,,IGN:2,,,,value,,UIN,,days,
r2,recovair,,BypassPosition,bypass flap position,,,b509,290900,ign,,IGN:2,,,,value,,UCH,,%,
r3,recovair,,HeatRecovery,heat recovery (kept on by the VAI),,,b509,290a00,ign,,IGN:2,,,,value,,UCH,1=on;2=off,,
r5,recovair,,StoveProtection,negative pressure protection for a stove (STOV),,,b509,294700,ign,,IGN:2,,,,value,,UCH,0=off;1=on,,
r9,recovair,,FlowCorrection,flow setpoint correction,,,b509,292000,ign,,IGN:2,,,,value,,D1B,,,Still unknown: 5a00/5b00 (3142) and 5c00/5d00 (2979). They're constant and not a speed limit, because the fan went above 3142.
Uh oh!
There was an error while loading. Please reload this page.
Hello,
I'm trying to integrate a Vaillant recoVAIR 275 using an eBUS Adapter Shield C6 and ebusd 26.1.
The device is detected correctly:
c0;Vaillant;WTW04;0127;9001
ebusd reports:
unable to load scan config c0:
no file from vaillant with prefix c0 matches ID "wtw04", SW0127, HW9001
Current status:
Relevant log:
scan c0: ;Vaillant;WTW04;0127;9001
unable to load scan config c0:
no file from vaillant with prefix c0 matches ID "wtw04", SW0127, HW9001
The repository contains:
vaillant/08.recov.csv
but it is apparently not matched automatically to WTW04.
Is WTW04 / SW0127 / HW9001 currently supported?
Is there a mapping or configuration file available?
Thanks.